system.tag.addTag
Adds a new tag in Ignition. You can add OPC, memory, expression, query, folder, and UDT instance tags. You can't add Client Tags, because those can vary from project to project.
Permission Type: Tag Editing
tip
system.tag.addTag(parentPath, name, tagType, dataType, accessRights, enabled, value, attributes, parameters, overrides, alarmList, alarmConfig)
StringparentPathThe folder to add the tag to. Leave blank for the root folder.
StringnameThe name of the tag.
StringtagTypeThe type of tag to create. Possible values are OPC, MEMORY, EXPRESSION, QUERY, Folder, and UDT_INST.
StringdataTypeThe data type of the tag. Not used for UDT instances or folders.
  • Possible basic values are Int1, Int2, Int4, Int8, Float4, Float8, Boolean, String, DataSet, and DateTime.
  • Possible array values are Int4Array, Int8Array, Float8Array, BooleanArray, StringArray, DateTimeArray.
StringaccessRightsThe access rights for a tag. Possible values are Read_Only, Read_Write, and Custom.
booleanenabledIf true, the tag will be enabled.
ObjectvalueThe value of the tag. Used for memory tags.
PyDictionaryattributesThe tag's configuration attributes.
PyDictionaryparametersThe parameters for a UDT instance tag.
PyDictionaryoverridesAll of the overrides for a UDT instance tag.
StringalarmListList of legacy alarms for the tag. The legacy alarm system was retired in 7.6.0, so the alarmConfig parameter should be utilized on newer versions.
PyDictionaryalarmConfigThe alarm configuration for the tag. See editAlarmConfig for details on how to use this parameter.
Nothing
All
note
If called in the Gateway scope, a tag provider must be specified.
Associated attributes:​
Complete list of the acceptable Tag Properties and alarmConfig.
Example #1 - Add OPC tag
system.tag.addTag(parentPath='', name="TagOPC", tagType="OPC", dataType="Int2",attributes={"OPCServer":"Ignition OPC-UA Server", "OPCItemPath":"[MLX]N7:0"})
Example #2 - Add OPC tag with two alarms
system.tag.addTag(  parentPath='',
name="TagOPCAlarm",
tagType="OPC",
dataType="Int2",
"OPCItemPath":"[MLX]N7:0"},
alarmConfig={ "Alarm":[
["name", "Value", "Alarm"],
["setpointA","Value", 1.0],
["CustomEmailSubject","Value","My Subject"]
"Alarm2":[
["name", "Value", "Alarm2"],
["parameterName", "Value", "newValue"],
["enabled", "Expression", "1=2"],
["CustomEmailMessage","Value","My Message"]
Example #3 - Add Folder
system.tag.addTag(parentPath='', name="Folder", tagType="Folder")
Example #4 - Add Memory tag
system.tag.addTag(parentPath='', name="TagMemory", tagType="MEMORY", dataType="Int2", value=25)
Example #5 - Add Memory tag with an Alarm using the alarmList parameter
alert = "myAlert;Medium_High;0.0;50.0;0;;;2.0;SEC$"
system.tag.addTag(parentPath = '', name = "TagMemory", tagType = "MEMORY", dataType = "Int2", value = 25, alarmList = alert)
Example #6 - Add Expression tag
system.tag.addTag(parentPath='', name="TagExpression", tagType="EXPRESSION", dataType="Int2", attributes={"Expression":"{[~]Tag1} * 20.5"})
Example #7 - Add Query tag
system.tag.addTag(parentPath='', name="TagQuery", tagType="QUERY", dataType="DateTime", attributes={"Expression":"SELECT CURRENT_TIMESTAMP", "SQLBindingDatasource":"MySQL"})
Example #8 - Add Memory tag to a provider other than the default tag provider
system.tag.addTag(parentPath="[ProviderName]Folder", name="TagMemoryProvider", tagType="MEMORY", dataType="Int2", value=42)
Example #9 - Add UDT instance tag
# Before running this script, there must be a UDT named 'Motor'
# that has a string parameter 'DeviceName' and an integer parameter
# 'MotorNumber'.
system.tag.addTag(parentPath='', name="TagUDT", tagType="UDT_INST", attributes={"UDTParentType":"Motor"}, parameters={"DeviceName":"CLX", "MotorNumber":1})
Example #10 - Add UDT instance tag and override multiple parameters on status tag
# Before running this script, there must be a UDT named 'SecondUDT'
# that has a string parameter 'DeviceName', an integer parameter
# 'MotorNumber', and a tag named "STATUS".
system.tag.addTag(parentPath='', name="TagUDTParameters", tagType="UDT_INST", attributes={"UDTParentType":"SecondUDT"}, parameters={"DeviceName":"CLX", "MotorNumber":2}, overrides={"STATUS":{"ScanClass":"Default Historical", "Enabled":"false"}})
Example #11 - Add UDT instance tag and override the scan class of a tag inside of another UDT
# Before running this script, there must be a UDT named 'ThirdUDT'.
# ThirdUDT must contain a UDT 'SecondUDT',
# which has a string parameter 'DeviceName', an integer parameter
# 'MotorNumber' and a tag named "STATUS".
# Note the nested SecondUDT has the name 'Child_Instance' in the ThirdUDT.
system.tag.addTag(parentPath='', name="TagUDTScanClass", tagType="UDT_INST", attributes={"UDTParentType":"ThirdUDT"}, parameters={"Motor/DeviceName":"CLX", "Motor/MotorNumber":1}, overrides={"Child_Instance/STATUS":{"ScanClass":"Default Historical"}})
Example #12 - Create a memory tag with a type of DataSet, and pass in a dataset as the initial value of the newly created tag
# create an intial dataset to pass the tag
initData=system.dataset.fromCSV('"#NAMES"\n"Col 1"\n"#TYPES"\n"I"\n"#ROWS","1"\n"0"\n')
# create the tag
system.tag.addTag(parentPath='', value=initData, name="TagMemoryDataset", tagType="MEMORY", dataType="DataSet")
Example #13
# Example: Add an Array type Memory tag to the default tag provider
# create a dataset
dataset = system.dataset.toDataSet(["values"], [[1],[2],[3]])
# create the tag
system.tag.addTag(parentPath='', name="TagMemoryArray", tagType="MEMORY", dataType="Int4Array", value=dataset)