OPC UA Connections

OPC Connection Status​

The OPC Connections page displays all currently configured OPC (both UA and DA) connections, as well as their status. If any are faulted, you can click the red faulted status to get an error message popup with a full description of the error.

PropertyDescription
NameOPC server name.
TypeOPC server type - UA or DA
DescriptionA short description of the OPC UA connection.
UptimeTotal time OPC server is connected.
EnabledTrue or false value whether the device connection is enabled.
StatusCurrent status of OPC server.

Diagnostic Information​

Diagnositic information for each OPC connection is displayed on the Connections Details panel, separated by Server and Client tabs. The Server Diagnostics tab displays server status, build info, and server diagnostics. The Client Diagnostics tab displays subscription information for that particular server. It will list out all of the subscriptions to that server with the publishing rates, as well as the number of items within that subscription.

To access the Connections Details panel:

  1. Go to Connections > OPC > Connections.
  2. Click the three dots menu next to a connection and select View Details.

Now you can switch between the Server Diagnostics tab and the Client Diagnostics tab to monitor information as desired.

Server​

By default, server diagnostics are disabled since they can generate a considerable amount of network overhead and impact performance. To begin tracking server diagnostics, click Enable Server Diagnostics on the Server Diagnostics tab. Note that not all OPC UA servers support server diagnostics.

OPC Connections Page - Server

Changed in 8.3.9
Due to a Milo 1.1.6 upgrade, the OPC UA server library now enforces users to hold a ConfigureAdmin or SecurityAdmin role when enabling server diagnostics. New installations for versions 8.3.9+ will grant a ConfigureAdmin role to the default opcuauser automatically. If you have upgraded from 8.3.8 and earlier to 8.3.9 or later, this role will need to be manually added to the opcua-module User Source. See the Granting Roles section for more information on how to add ConfigureAdmin and SecurityAdmin roles.

A View Session Diagnostics option will appear when server diagnostics are enabled. Selecting this will allow you to inspect session and subscription activity.

Granting ConfigureAdmin or SecurityAdmin Roles​

When updating from 8.3.8 and earlier, you will need to manually add either a ConfigureAdmin or SecurityAdmin role to be able to use the Enable Server Diagnostics option for OPC connections. Only one of these roles is required, but both can be assigned. This process is not needed with new installs of versions 8.3.9 and later. Once the role has been assigned, the OPC connection will need to be reconnected to apply the permission changes.

The following process describes how to add a ConfigureAdmin role to the opcuauser within the opcua-module User Source, and then start tracking server diagnostics. The same steps can be followed to add the SecurityAdmin role.

  1. Navigate to Platform > Security > User Sources.
  2. Expand the three dots menu for the opcua-module User Source and select Manage Users.
  3. Click the Roles tab.
  4. Click Create Role +.
  5. Enter ConfigureAdmin in the Role Name field.
  6. Click Create Role.
  7. Return to the User tab.
  8. Expand the three dots menu for opcuauser and select Assign Roles.
  9. Check the box for ConfigureAdmin.
  10. Click Save Changes.
  11. Navigate to Connections > OPC > Connections.
  12. Expand the three dots menus to Disable and then Enable OPC connections so that the new role will take effect.
  13. Select View Details from the connection's three dots menu once the status returns to Connected.
  14. Click Enable Server Diagnostics.

Client​

The Client Diagnostic tab subscription list can be filtered by search criteria, viewed based on a specified number of subscriptions per page, and refreshed as needed to see the latest subscription data. The table below describes the information displayed for each subscription.

PropertyDescription
NameDisplays the subscription name.
RateThe rate defined in the Tag Group, used as the requested sampling interval for monitored Items belonging to the corresponding subscription.
Request Publishing IntervalThe rate a subscription will report accumulated change notifications at. The interval is derived from Rate, unless explicitly defined.
Revised Publishing IntervalThe server's revised rate for accumulated change notifications.
Tag CountThe number of tags currently subscribed to that Tag Group.

Nodes​

To monitor subscriptions and diagnostics from the Client Diagnostics tab, expand a group to see the monitored node details. Clicking the dropdown arrow for any of the subscriptions will open the list of subscribed OPC items.

PropertyDescription
Node IDThe OPC item path.
Requested Sampling IntervalThe rate the underlying tag/node will be polled at.
Revised Sampling IntervalThe revised rate at which the underlying tag/node will be polled at.
Requested Queue SizeDetermines how many data points can be stored and transferred to the client once the sampling rate elapses when the sampling rate is slower that the publishing rate.
Revised Queue SizeThe revised amount of data points that can be stored and transferred to the client once the sampling rate elapses when the sampling rate is slower that the publishing rate.
Status CodeStatus of the node.

Configuring an OPC Client Connection​

An OPC UA connection is used to communicate with an OPC UA compliant server, such as the one the OPC UA Module provides.

The following steps walk through connecting Ignition (as an OPC UA client) to a OPC UA server. For information on connecting to a third party server, refer to the Connecting to Kepware OPC UA page for an example.

  1. On the Connections section of the Gateway Webpage, go to OPC > Connections. The OPC Connections page is displayed.

  2. Click on Create OPC Connection +. A popup wizard will appear.

    Configuring OPC Client Connection Step 2

  3. Select OPC UA Connection from the list and click Next. The Server Discovery page appears.

  4. Enter an OPC UA endpoint URL for the OPC UA server Ignition should connect to. The format should be as follows:

    opc.tcp://IpAddress:Port

    Alternatively, you can use a host name instead of an IP address:

    opc.tcp://myServer:12345
    note

    Using the Skip to Advanced Configuration link on the bottom right of the popup will allow you to manually configure connection settings. This is useful in cases where a server does not allow anonymous endpoint access, but provides separate discovery endpoints.

  5. Click Next.

  6. Choose a server, then click Next.

    Configuring OPC Client Connection Step 6

  7. Choose an endpoint, then click Next.

    Configuring OPC Client Connection Step 7

  8. A summary of your selections thus far will be displayed. Once you confirm your settings, click Next.

    Configuring OPC Client Connection Step 8

  9. A Manage Certificate window will open if you haven’t previously trusted a certificate. Trust the certificate and click Next. If the certificate that the Endpoint sends you to is already in Ignition’s trust store, this step is skipped.

  10. If you entered a discovery URL in step 4, you also have an option to enter another URL if the host is unreachable.

  11. Select a Security Policy and Message Security configuration to use when connecting to the endpoint, then click Finish. The policies that appear here are determined by the server.

  12. On the Configure Connection page, give the connection a name. Some OPC UA servers may also require specific Authentication credentials. Check with the OPC UA server's documentation for more details. Credentials for Ignition's OPC UA server can be found on the Ignition's OPC UA Server page.

    Configuring OPC Client Connection Step 12

  13. Once all desired settings have been configured, click Create OPC Connection.

Ignition is now connected to the OPC UA server.

OPC UA Client Connection Settings​

The following tables describe all the available properties.

Main​

PropertyDescription
DescriptionShort description of this connection.
EnabledDisable the connection to the OPC server.
Read OnlyPuts the connection into read-only mode. All writes sent to this server will fail.

Authentication​

PropertyDescription
Authentication Type
Changed in 8.3.3
The Authentication Type field has replaced the Username/Password fields to additionally provide Anonymous and Certificate selections. Once an option has been chosen, relevant sub properties based on the Authentication Type will display.
  • Username: Requires a user and password to authenticate the connection. This is the default type.
      Username: A username the connection will use when authenticating with the UA server.
      Password: The password to use when authenticating with the UA server. You can select between None, Embedded, or Referenced.
  • Anonymous: Allows authentication for this OPC UA connection anonymously.
  • Certificate: Enables X.509 certificate-based authentication for this OPC UA connection.
      Certificate Pem: The PEM encoded X.509 certificate that this OPC UA client will use for Session authentication.
      Private Key Pem: The PEM encoded private key in PKCS1/PKCS8 format. You can select between Embedded or Referenced.

Keep Alive​

PropertyDescription
Keep-Alive Failures AllowedThe allowed number of consecutive failures before disconnecting. A zero or negative value will not cause a disconnect. Default is 1.
Keep-Alive IntervalThe interval between keep-alive requests, in milliseconds. Default is 15,000.
Keep-Alive TimeoutThe maximum duration to wait for a response to a keep-alive request, in milliseconds. Default is 10,000

Advanced​

PropertyDescription
Host OverrideWhen specified, if the endpoint address returned by the OPC server has a different IP address or hostname than the discovered endpoint, the overridden value will be used. Expects just an IP address or hostname, for example: 192.168.1.10
Connect TimeoutThe timeout, in milliseconds, when opening a socket connection to a remote host. Default is 5,000.
Acknowledge TimeoutThe timeout, in milliseconds, to wait for an Acknowledge message in response to the client's Hello message. Default is 5,000.
Request TimeoutMaximum amount of time, in milliseconds, to wait for the response to a request. Default is 60,000.
Session TimeoutRequested session timeout value, in milliseconds. Default is 120,000.
Max Per OperationSpecify the maximum number of nodes to read, write, subscribe, or unsubscribe to in any given UA server request. Default is 8,192.
Max References Per NodeConfigures the number of references per node. A "node" in this case is any item inside of a UA server, so items like tags and folders would qualify as a node, while references simply means a reference to another node.
This setting is useful in situations where the address space is completely flat, so a large number of adjacent nodes could potentially run into a maximum message size. In these cases decreasing the value of this property can be useful. However, most systems will not need to change this setting. Defaults to 8,192 references.
Max Pending Public RequestsThe number of concurrent Publish Requests allowed to be pending at any given time. Default is 2.
Max Notifications Per PublishThe maximum number of notifications per publish. Default is 65,535.
Max Message SizeThe maximum allowable size of an OPC UA application layer message. Default is 33,554,432.
Max Array LengthThe maximum allowable size for arrays. Default is 2,147,483,647.
Max String LengthThe maximum allowable size for strings. Default is 2,147,483,647.
Deprecated Data Type Dictionary SupportWhen enabled, the deprecated DataType Dictionary mechanism will be used to decide custom DataTypes, instead of the DataTypeDefinition attribute.
Browse OriginThe Node that browsing should originate from. Options are OBJECTS_FOLDER or ROOT_FOLDER. Most OPC UA Servers use OBJECTS_FOLDER, but some non-standard servers may require ROOT_FOLDER to browse correctly. Ignition's OPC UA Servers uses OBJECTS_FOLDER.
Timestamp Source
New in 8.3.1
The source to use for timestamps in values from this connection. Options include:
  • IGNITION
  • OPC_PREFER_SERVER
  • OPC_PREFER_SOURCE

Failover​

PropertyDescription
Failover EnabledEnable failover on the connection, allowing the UA client to switch to a backup server in the event the primary server is unavailable.
Failover ThresholdThe number of retry attempts before the failover connection is used. Default is 3.
Failover Discovery URLThe discovery URL for the backup server's OPC UA server. Expects the following format:
opc.tcp://hostname:port
Failover Endpoint URLThe endpoint of the failover server. Example:
opc.tcp://192.168.1.0:62541
Failover Host OverrideWhen specified, if the endpoint address returned by the failover OPC server has a different IP address or hostname than the discovered endpoint, the overridden value will be used. Expects just an IP address or hostname. Example:
192.168.1.10

Security​

PropertyDescription
Certificate Validation EnabledEnables validation of server certificates. This is required by the OPC UA specification, but it may be disabled for troubleshooting or temporarily connecting to servers with invalid or untrusted certificates. Default is true.
Caution: Disabling certificate validation compromises the security of the connection.
Keystore AliasThe alias of the certificate and private key stored in the client KeyStore.
PasswordThe password to use when authenticating with the UA server. You can select between None, Embedded, or Referenced.

Failover Versus Backup Properties​

The Failover properties should be used when a single Ignition Gateway needs to connect to a pair of redundant OPC UA servers. The failover OPC UA server will be used in the event the primary OPC server goes down. To enable failover, set the Failover Enabled property to true, and specify the Failover Discovery URL, Failover Endpoint URL, and Failover Host Override. The Failover Threshold can be adjusted if desired.

note

Failover events are "sticky." That means once control has moved to a backup OPC UA server, it stays there until that server fails.