Version: 8.1
Connecting to Logix
note
This driver is optimized for Logix family devices with firmware version 21+, but supports earlier firmware versions with significantly reduced performance.
Inductive University
Connecting to ControlLogix v21
Watch the video
Connect to an Allen-Bradley Logix Device​
  1. Go to the Config section of the Gateway Webpage.
  2. Scroll down and select OPC UA > Device Connections.
    Connect to Logix Step 2
  3. On the Devices page, find the blue arrow and click on Create new Device.
  4. Select Allen-Bradley Logix Driver, and click Next.
    Connect to Logix Step 4
  5. Fill in the following fields:
    • Name: CLX
    • Hostname: type the IP address for the PLC, for example 10.20.1.54.
    Leave the default values in the remaining fields.
    Connect to Logix Step 5
  6. Click Create New Device.
  7. The Devices page is displayed showing the ControlLogix device is added to Ignition. The Status will show as Disconnected and then Connected.
    Connect to Logix Step 7
  8. To see all the Tags, go to OPC Client > Quick Client in the Config section. On the OPC Quick Client page, expand the CompactLogix folder and in the Global folder you can see all the tags.
Driver Implementation​
One noteworthy implementation of the Logix driver is how boolean arrays are handled. Boolean arrays items are browsed as members of a 32-bit DWORD. Thus, a BOOL[64] in the PLC is implemented as DWORD[2] in the driver.
Below is a table representing how members of a boolean array items are mapped in the PLC, compared to the Logix driver's implementation.
PLC MappingDriver Implementation
boolTag[0]boolTag[0].0
boolTag[31]boolTag[0].31
boolTag[32]boolTag[1].0
boolTag[63]boolTag[1].31
New in 8.1.28
The Logix driver also supports the following datatypes:
  • DT (Date/Time)
  • LDT (Date/Time [ns])
  • LTIME (LTime [ns])
  • TIME (Decimal)
  • TIME32 (Time32 [us])
Device Connection Settings​
The General settings are common to all Allen Bradley devices, and the Connectivity settings are device dependent.
General​
NameDescription
NameThe user-defined name for this Device. The name chosen will show up in OPC Item Paths and under OPC-UA Server > Devices of the Configure page of the Gateway. The Device Name must be alphanumeric.
DescriptionThe user-defined description for the device. This is only used as a note to differentiate between devices.
Enable DeviceOnly devices that are enabled appear in Connections > Devices of the Status page of the Gateway and thus have their tags available for use.
Connectivity​
NameDescription
HostnameThis is the IP Address of the ControlLogix Ethernet module (1756-ENET) to route through to connect a ControlLogix processor. EthernetIP protocol on TCP port 44818 (0xAF12) is used to communicate to ControlLogix processors.
PortPort to connect to the remote device.
Local Address
New in 8.1.8
The local address to connect from when establishing a TCP connection. If left blank, then the driver will simply pick an available address.
TimeoutAfter sending a request to the ControlLogix processor, the Communication Timeout setting is the amount of time in msec to wait for a response before treating it as a failure.
Max Concurrent RequestsThe number of requests that Ignition will try to send to the device at the same time. Increasing this number can sometimes help with your request throughput, however increasing this too much can overwhelm the device and hurt your communications with the device.
Slot NumberThe Slot Number value is the zero based ControlLogix chassis slot number of the ControlLogix processor to connect to.
Connection PathIf specified, the slot number setting is ignored for this connection path to the processor. Be sure to terminate the path with backplane and slot number.
Advanced​
NameDescription
Automatic RebrowseMonitor for tag additions and UDT changes and automatically initiate a re-browse when detected. If this is disabled tags will only be browsed when connecting and reconnecting. (Default is true.)
Identity Request Frequency
New in 8.1.3
Frequency, in milliseconds, that the request to read CIP Identity Object attributes occurs at. (Default is 5,000.)
CIP Connection SizeThe CIP connection size to use during Forward Open requests. (Default is 500.)
CIP Connection Timeout
New in 8.1.10
Target timeout, in milliseconds, for CIP connections and RPI. (Default is 16,000)