Ignition’s data historian functionality is a robust set of features that are built into Ignition modules, providing data acquisition, storage, retrieval, and visualization.

As with everything else in Ignition, historian functionality is modular. Several modules are often used together to provide a complete system. Often, users combine Ignition’s historian functionality with SCADA, HMI, IIoT, ERP, or MES functionality.

Although many people think of Ignition’s Tag Historian Module as the “Ignition Historian,” a full data historian often is described by not only storing tag data, but also storing event-based data and providing visualization. As such, this document covers the modules for those features.

Modules​

One possible configuration of modules when Ignition is used as a data historian.

Ignition’s modular architecture allows for the choice between using a single module or using multiple modules for a given installation. The bare minimum needed to use Ignition as a tag historian is the Tag Historian Module. However you can incorporate more modules, especially if event-based storage is needed or direct device communication will be used. The modules that are used in a typical system are outlined next.

Tag Historian Module​

This provides storage and retrieval of historical data through Ignition’s tag system. Incoming tag changes can be piped to data storage, and tag history can be retrieved through the module.

  • Storage: Storage of data by the Tag Historian Module can go to several locations. Internal storage is available to store small amounts of data within Ignition itself. SQL-based storage is the normal recommendation for most systems and pipes data through to an attached SQL database. Additional storage engines are available from third-party developers, some of which can be found on the Module Showcase. Regardless of the storage engine, the Tag Historian Module offers tools for data storage rates, compression, deadbands, and a number of other features.
  • Retrieval: The Tag Historian Module can be used to retrieve history and perform calculations and aggregations on historical data. Depending on the storage engine being used, the Tag Historian Module will either perform the retrieval directly and perform any appropriate aggregates, or in the case of using third-party storage engines, the Tag Historian Module will pass the request through to the storage engine.

SQL Bridge Module​

This module provides Transaction Groups, which are used for event-based logging. Data is stored into SQL database tables and options are provided for storing quality codes, timestamps, auto creating configured tables, data rates, scheduling, and more.

OPC UA & Driver Modules​

These modules provide data collection. The OPC UA Module acts as the foundation for Ignition’s drivers, which offer native communication to a large number of devices. It should be noted that Ignition can also connect to third-party OPC servers for data collection, either through the platform for OPC UA connections or through the OPC COM Module for OPC DA connections.

MQTT Transmission, Distributor, and Engine​

These IIoT modules can be an integral part of data collection when using modern architectures. MQTT Engine plugs right into Ignition’s Tag Historian Module to feed data. It also includes event storage through DRecords, which place data in database tables to create records similar to Historical Transaction Groups.

Perspective/Vision Module​

Sometimes visualization is part of a requirement for data historians. Perspective and Vision are visualization systems that provide simple, easy-to-use screen building tools to create dashboards, desktop applications, web pages, and on-screen reports.

Reporting Module​

Although often not included in a data historian, the Reporting Module is worth mentioning, since it allows for generation and automatic PDF reports to send directly from within Ignition.

Ignition Platform​

Although this isn’t a module, the platform itself is worth noting as it provides a number of features. In addition to providing the required subsystems, like the tag system, the Ignition Platform also provides scripting support to react and respond to tag changes in real time and includes an expression language that allows for tags based on equations or calculations.

Data Storage​

Data storage of event-based data through SQL Bridge is stored in SQL databases. SQL Bridge allows users to define table names and columns, and choose what to store depending on identified triggers. Historical Transaction Groups are a good choice for most event-based logging.

Data storage of tag-based data through Tag Historian can go to several locations. Most users target a SQL database, but other possibilities include small internal storage systems and third-party storage engines.

Data Retrieval​

Using Ignition’s Visualization Tools​

When using Perspective or Vision, Ignition provides a nice set of built-in tools for data retrieval. For Tag History, this includes Tag History bindings, a data source type for the Reporting Module, automatic integration with some charting components, and drag-and-drop configuration within the design tools. For event data that’s stored to a SQL database, Ignition has Named Queries that allow for retrieval including support for conditions, date and quality limitations, and any other options SQL syntax allows.

Using External Tools​

For event data, external tools can query the database directly, which makes everything accessible to parties that have appropriate security permissions.

For tag historian data, it is recommended that external tools query data from Ignition’s APIs. This is useful as any data retrieval will go through Ignition’s logic that provides interpolation, aggregation, partition spanning, and any other logic needed. The API function for retrieving this data is system.tag.queryTagHistory(), and setting up a REST endpoint for that function is simple using the WebDev Module.

It should also be noted that Ignition’s automatically-created database tables are fully and publicly documented for users who prefer to directly query the tables instead of use the recommended queryTagHistory() function.

Architectures​

The following architectures are based on Ignition running with the Tag Historian Module targeting a SQL database. Architectures using different tag history storage could look significantly different. For example, the open source, free Azure ADX connector written by Microsoft has very high throughputs and stores to the cloud, so no SQL database is used.

If using a SQL database for storage, these architectures can provide a sense of possible configurations. See the Benchmarking section to get a sense of the possible throughputs for different database technologies.

  • Standard Architecture: The Standard architecture is as straightforward as Ignition running on one server and the SQL database running on the second server.

  • High Resilience Standard Architecture: This architecture configuration adds a change to the database server by installing Ignition with only the Tag Historian Module alongside the SQL database. This offers a few advantages like high speed Gateway Network communication between servers and the ability to weather communication difficulties, latency, and packet loss well.

  • High Performance Multi-Database Architecture: This architecture includes 3 or more servers, where the added servers replicate the database server as described in the High Resilience Standard Architecture. In addition to the communication advantages, this configuration also allows scaling past single database throughput limit.

  • IIOT Architecture: This architecture is geared towards collecting data from edge devices and centrally storing that data for further comparison and analysis. In this configuration, PLCs or other devices communicate with data collectors in the field. These data collectors could be Ignition, Ignition Edge, or systems that speak MQTT natively. Additionally, some devices speak MQTT natively with data buffering and store and forward technologies available. Since these devices use the light-weight, efficient, and secure MQTT protocol, they can often communicate directly to the central Ignition platform. Depending on the industry, collectors are optional. They do however make sense from a bandwidth, network segmentation, and security standpoint.

Benchmarking​

Event-based data and tag-based data both need to have appropriate hardware and software to support the needs of the design. However, an appropriately designed system generally has thousands of times more tag-based data than event data. As such, the benchmarks here are focused on tag historian data and throughputs.

Understanding Rates and Change Percents​

Ignition’s tag historian performance is best rated in tag changes per second. At a 10sec rate, with 10% of tags changing, 100 tags produce 1 tag change per second.

For example, the following table outlines the storage and change rates with the number of tags for a database that can handle 10,000 tags.

Example Database Tags​

Storage Rate10sec60sec1sec1sec
Change Rate10%10%10%100%
Number of Tags1 Million6 Million100 Thousand10 Thousand

Number of Tags​

The Example Database Tags table demonstrates how the amount of tags a single database can handle heavily relies on the storage rate and the change rate of the tags. Ignition systems are configured by default to use 10sec storage rates for tags. However, some users prefer 1sec rates or faster for some or all tags. Increasing rate speed is supported and encouraged as needed. Keep in mind, faster rates will equate to more changes per second going to the database.

SSD vs HDD​

Inductive Automation highly recommends using an SSD both for the Ignition installation and for the database storage if medium-low, medium, or high throughputs are expected. If only low history throughputs are expected, an HDD may suffice. If choosing an HDD, testing the database’s throughput is recommended to ensure an HDD will handle the required storage speeds.

Internal Historian​

The internal historian is a disk-based historian, available directly inside Ignition. This can be a great way to store a small amount of data at remote locations or locations where a SQL database isn’t available.

The data is set to be limited by default to one week. Although that limit can be expanded, Inductive Automation doesn’t recommend storing years of data in the internal historian, as the internal historian is only intended for small amounts of local history. If you calculate out your needed timeframe to log, your rates, and your change percent, we recommend keeping the total records around 10 million rows. Since the internal historian doesn’t have some of the advanced features of the SQL Database storage like automatic partitioning, anything planned for storing over 10 million records should use SQL Database storage or another storage engine.

Tag Changes Per Second​

In order to provide benchmarks that are meaningful, these benchmarks are rated in Tag Changes Per Second. Please estimate your Storage Rate and Change Rate, and multiply them together to calculate your tag changes per second.

Tag Changes Per Second
Tag Count * Change Rate Percent / Storage Rate (in seconds)

For example, 100,000 Tags * 20% changing / 5 sec storage rate = 100,000 * .2 / 5 = 4,000 tag changes per second.

SQL Database Benchmark Estimates​

CategoryData
PlatformWindows
CPUIntel Core i7-4790K (4/8 core, 4GHz)
RAM16GB
DriveSamsung SSD 860 EVO 2TB

Estimated Steady State Throughput (tag changes/sec)​

caution
  • These benchmarks are estimates only. Hardware differences and many other factors can have a significant impact on throughputs.
  • These estimates are based on steady state throughputs. Having reasonable Ignition Tag Historian partition sizes configured will help to keep performance from degrading in most databases. Timescale is the exception on this list, as it doesn’t experience degradation over time.
  • Oracle isn’t included on this list as Inductive Automation does not have an Oracle enterprise license. The lightweight Oracle Express was tested and had similar performance to MySQL, but it’s expected a full version of Oracle would have significantly better performance.

Initial Write Throughput (tag changes/sec) Across Databases​

These Initial Write benchmarks are included just for reference. Most databases have high performance on initial throughput and that speed then drops until they reach a steady state. If you’re running your own tests and the initial results are showing higher throughput, be sure to let the system run for a few hours or a few days to let the rates even out.

Storage Space Requirements​

Uncompressed, unoptimized storage requirements in SQL databases take around 100 bytes per tag change, regardless of the database chosen.

Based on that number, it’s fairly easy to calculate storage requirements.

Storage Space Requirements
Tag changes per second * 100 * seconds in time period

For example, if you have 1,000 tags with 10% changing and at a 10s rate, you’re looking at 10 tag changes per second. Multiply that by 100 bytes and 86,400 seconds in a day, and you get around 86.4 MB per day.

Note that many databases have compression options, which can reduce the overall storage required by 30-50% or more, generally at the cost of CPU/throughput. Timescale, specifically, has an option that claims to reduce storage by up to 90% in certain circumstances. If storage space is a main constraining factor, it may be worth exploring these options.

Throughput vs Network Quality​

The following network quality throughput testing was performed using Microsoft SQL Server. It is believed to be a reasonable expectation that other databases follow similar performance characteristics when it comes to network latency. This testing was performed with large numbers of tag changes at a one-second rate.

Standard Architecture​

Latency (Server 1 to Server 2)
Dropped Packets0ms1ms5ms10ms20ms50ms100ms150ms200ms
0%2243322---
2%2243322---
5%101111----
10%1--------
15%---------
20%---------

High Resilience Standard Architecture​

Latency (Server 1 to Server 2)
Dropped Packets0ms1ms5ms10ms20ms50ms100ms150ms200ms
0%303030303030302620
2%303030303030191412
5%3030303030191197
10%302221201710975
15%20141312117653
20%5---6----

Ignition is much more resilient in Scenario 2 using the High Resilience Standard Architecture, where a performance degradation can’t be seen until there are a significant percent of dropped packets or over 100ms latency.

Optimization​

SQL Bridge​

These optimizations may apply to all systems.

  • Configure data pruning on tables that don’t need to store history forever.
  • Ensure triggers are used to store events properly.
  • Don’t store data that’s not needed. If time series storage is needed, consider using tag historian instead, and logging events through Transaction Groups.
  • When writing queries against the data stored by SQL Bridge, look at the WHERE clause of the queries and create appropriate indexes in the database tables.
  • Monitor the system for performance, to ensure you didn’t miss adding an index or that database table size isn’t excessive for the project and the hardware it’s running on.

Tag Historian Using SQL Databases​

These optimizations may apply to all systems.

  • Set reasonable deadbands for tags. Deadbands make sure that junk data isn’t logged. If a sensor has an accuracy of 0.2, there’s no reason to ever log a change of 0.02, since that change is just noise. Setting reasonable deadbands can save a significant amount of storage space and throughput from logging noise.
  • Set time deadbands (“Min Time Between Samples”) as it makes sense, so tags don’t log faster than specific rates.
  • Set tag rates appropriately. Only set tags to log at 1sec rates if needed. Default to slower rates unless requirements dictate otherwise.
  • If it makes sense for your system, we recommend turning off Stale Data Detection. If the system is running slower than it feels it should be, check the sqlth_sce table. If there are more than a few hundred rows, you may have inadvertently overloaded the system. Turning off the Stale Data Detection is normally a safe thing to do (under the advanced properties in the database connection), but read the user manual to make sure you understand the setting first. Turning that setting off will keep the sqlth_sce table from growing if the system is experiencing slowness.
  • If using MySQL, add an extra connection parameter to the database connection. This will increase throughput from around 1,000 tag changes per second to around 10,000-20,000. rewriteBatchedStatements=true.
  • Ensure no other applications or services are running on the systems where Ignition and the database(s) are hosted.
  • Tune partitions to keep from exceeding 100m to 1b rows per partition. Keeping partition sizes reasonable makes queries over short time frames faster, and helps ensure dashboard charts and graphs render relatively quickly.
  • Set up pre-processed partitions if querying over longer periods is expected. Note that doing so will require some additional storage and processing, which will impact the overall achievable storage throughput marginally.

High Throughputs​

These optimizations apply if you have a system spec’d or in production where you are expecting high throughput in terms of tag changes per second.

  • Option 1: Reduce throughput following the guidance above.
  • Option 2: Add another database/schema to the SQL database DBMS on the same storage. Multiple databases can help split the load, and can increase throughput. Set some tags to go to one database, and other tags to go to the other database.
  • Option 3: If throughputs still aren’t achievable, putting multiple databases on the same DBMS, but pointed at different storage can also increase throughputs. Some databases are heavily limited by drive IO, and splitting databases to different storage can have a significant impact.
  • Option 4: Pointing Ignition at multiple database servers will ensure separate throughput to each server, which effectively doubles the possible throughput that comes from a single database server.
  • Option 5: Consider a distributed architecture. If there are multiple sites and a central system, consider keeping site data at each site, and sending summary data to central. Don’t worry; if you’re using the Gateway Network, you can always access site tag historian data from the central system, treating all the connected Ignition gateways as a large distributed system. Central reports, dashboards, and other visuals can stream data from the sites to display it centrally, as long as the site is online.
  • Option 6: If very high throughputs are required, in the 500,000 to 1,000,000 tag changes per second range for example, this may exceed what is practical with a set of SQL databases. Other storage engines are available for Tag Historian from the Module Showcase and other areas that have extremely high throughputs. These options may be worth considering when very high throughputs are needed.

Reducing storage space requirements​

  • Database Compression (30-50%)
    • Many databases have options to compress data for tables.
  • Full Drive Compression
    • Drive compression for storage drives can also provide benefits.
    • Not normally used together with Database Compression.
  • If using Timescale
    • Timescale’s Chunking & Compression can provide even more significant savings. Compression happens after a configurable time period. Drive space savings happen after that period has elapsed and trigger the compression. Savings are promoted as up to 90% or more. Inductive Automation has not run benchmarks, so the exact savings against the Tag Historian table data is unknown at this time.
  • Using other storage engines
    • Some storage engines have significant space savings.
    • Examples:
      • Influx from Module Showcase has smaller storage requirements per record.
      • Azure ADX’s has very high throughput support and is supposed to have efficient storage. Microsoft has released a free, open source module as a connector, which can be found on GitHub. The Azure ADX service is a paid service from Microsoft.
    • Although Inductive Automation may provide guidance to module authors from time to time, Inductive Automation is not able to provide support for Module Showcase modules. We encourage customers exploring these to contact the module authors and explore any module documentation before making a decision to use one of these modules.

Security​

Security Hardening Guide​

Inductive Automation has a strong focus on security and provides guidance on securing individual Ignition Gateways. Inductive Automation recommends referring to the latest Security Hardening Guidelines for the latest in securing an individual Ignition Gateway.

Encryption in-flight​

Encryption in-flight can be an important consideration for any historical data. Ignition can run over secured networks, and all data transfer can run over VPN or other encrypted tunnels that support normal IP traffic. Additionally, Ignition client-to-server communication can be encrypted, Gateway-to-Gateway communication can be encrypted, and Gateway-to-Database traffic can be encrypted for all major databases. Some devices themselves don’t support encryption or other security measures, so it’s important to consider how to secure that device communication. Sometimes the solution is to put a small data collection device next to the insecure hardware, running Ignition Edge or another piece of software, to keep unencrypted communication off of any networks. Other solutions include VLAN encryption and securing networks for unencrypted traffic using firewall rules, IDSs, and other security measures. Inductive Automation recommends working with security experts if any questions arise on device communication security.

Encryption at-rest​

Encryption at-rest can be accomplished by encrypting drives where data will be stored or encrypting database tables if using a SQL database for data storage. These encryption tools will be part of the database management tools. Encryption at-rest generally doesn’t require the drive that Ignition is running on to be encrypted, since Ignition does not act as the main storage medium. Depending on the traffic, performance, and settings in Ignition, there’s a chance that cached data in the Store & Forward system could be temporarily written to disk from Ignition. If this data is required to be encrypted at-rest, even while temporarily buffered to disk, then in that case it would be appropriate to encrypt the drive Ignition runs on as well.

Client security​

Client security is normally accomplished using TLS 1.2/1.3 encryption, which provides the same level of encryption as a typical banking website. Standard PKI certificates are used, and the steps for configuration are covered in the Ignition documentation. Refer to the Security Hardening Guide for guidance on enabling TLS in Ignition.