--- title: "Alarm Event Properties Reference" --- # Alarm Event Properties Reference > An alarm event is made up of many pieces of information. The state, value, time, and configuration data for the alarm are collectively known as the properties of the event. Alarm event properties fall into two categories: * Alarm event properties, which are created when an alarm becomes active, cleared, or acknowledged. * Alarm runtime properties, which exist only while the alarm event is in memory. You can extend either category with your own associated data, which can be configured on any alarm that already exists in a project. To learn more, see [Alarm Associated Data](alarm-associated-data/alarm-associated-data.md). For the properties you set when configuring an alarm, see the [Tag Alarm Properties](../../tags/tag-properties/tag-alarm-properties/tag-alarm-properties.md) page. For the alarm settings that apply to the entire Gateway, see the [Gateway General Alarm Properties](platform\alarming\gateway-general-alarm-properties\gateway-general-alarm-properties.md) page. Alarm event properties define how an alarm behaves, and you can reference them in: * Messages, such as the body of an email or SMS message. * Expressions, such as the binding of a different property, or an Expression block. * Alarm pipelines, where they can also be created as temporary variables, such as a counter. * Scripts, such as a Script block in an alarm pipeline. Reference a property by wrapping its binding or scripting name in curly brackets. For example, `{name}` returns the name of the alarm, and `{eventValue}` returns the value associated with the event. Expressions can also retrieve a property with the `getProperty()` function. Properties are always referenced the same way, but the value you get back depends on where that value comes from, and how long it lasts. An alarm event holds active event properties, clear event properties, acknowledged event properties, and runtime properties. The active, clear, and acknowledged properties are created when that type of event occurs, so the same property can exist more than once within a single alarm event. A bound configuration property or associated data, for example, is captured on both the active and clear events. When you reference a property, the alarm event returns the most recent value, so referencing a bound property named MyData while the alarm is active can return a different result than referencing it after the alarm clears. The [Alarm Journal](platform\alarming\alarm-journal\alarm-journal.md) stores the individual values separately. ## Alarm Event Properties | Event Properties | Binding/Scripting Name | Description | Datatype | |---|---|---|---| | Name | name | The name of the Alarm. | String | | Enabled | enabled | Specifies whether or not this alarm is evaluated by the system. Set to False to turn off the alarm state and all associated actions. | Boolean | | Priority | priority | The priority (or severity) of the alarm. Used for sorting/filtering. Numerical values are associated with each priority to make comparison easier. This property can also be referenced as a string with the following priority names. Diagnostic (0)Low (1)Medium (2)High (3)Critical (4) | Integer or String | | Display Path | displayPath | The unique path of the Alarm state. Used for display and browsing purposes. | String | | Active Pipeline | activePipeline | The pipeline (if any) that will be used to process active events generated by the alarm. | String | | Clear Pipeline | clearPipeline | The pipeline (if any) that will be used to clear events generated by the alarm. Used when the alarm goes into the Clear State. | String | | Active Delay | timeOnDelaySeconds | The amount of consecutive seconds that the alarm state must be True before the tag enters this alarm state. | Double | | Clear Delay | timeOffDelaySeconds | The amount of consecutive seconds that the alarm state must be False before the tag exits this alarm state. | Double | | Notes | notes | Free-form notes for the alarm state. | String | ## Alarm Runtime Properties Runtime properties exist only while the alarm event is live, meaning it has not yet cleared or been acknowledged. They are not stored in the Alarm Journal by default. In addition to the properties you create through the Set Property block, the system defines the runtime properties below. The system uses these internally, but they are still regular properties, so you can access and modify them through the normal means. | Runtime Property | Description | Datatype | |---|---|---| | IsInitialEvent | Set to true when the event is caused by the initial state of the alarm. | Boolean | | SystemAck | Set to true when the alarm has been acknowledged by the system, due to an overflow of the live event queue. Live events are alarm events that are active or not acknowledged, and are limited for each alarm by the general alarm settings. | Boolean | | ShelfExpiration | When the shelf will expire for this event. | Integer | | IsShelved | Whether the alarm is currently shelved. | Boolean | | EventCanceled | If set, the event will drop out as soon as possible from the pipelines. | Boolean | | EventId | The unique id (uuid) of this alarm event. Each event gets a completely unique id. | String | | Source or Source Path | The qualified path to the item that generated this event. Includes the tag provider, tag path, and the name of the alarm. Example: prov:tagProviderName:/tag:folder/tagName:/alm:alarmName | String | | DisplayPathOrSource | Gets the display path if defined, otherwise, returns the source. | String | | State | The current overall state of the alarm. States include: Clear and Unacked (0)Clear and Acked (1)Active and Unacked (2)Active and Acked (3) | Integer | | EventState | The transitional state that caused the current event. States include: Active (0)Clear (1)Acknowledged (2) | Integer | | EventValue | The value associated with the current event. | Integer | | AckUser | The user who acknowledged this event. | String | | IsAcked | True if the event has been acknowledged. | Boolean | | IsActive | True if the event is still active. | Boolean | | IsClear | True if the event is not still active. | Boolean | | ActiveTime, ClearTime, AckTime | The timestamp for each event. | Date | | PipelineTransitionCount | How many transitions the event has made inside of the pipelines. | Integer | ## The PyAlarmEvent Object Some system functions, such as [system.alarm.queryStatus()](appendix\scripting-functions\system-alarm\system-alarm-queryStatus.md), return PyAlarmEvent objects. Each PyAlarmEvent object contains methods that retrieve additional information about an individual alarm. Many of these methods return a complex object instead of a standard Python datatype. In these cases, normal Python type casting turns the object into a native Python type. For example, `getDisplayPath()` returns a `StringPath` object, which the `str()` function converts to a Python string. The following example prints the display path, state, and acknowledgement status of each active alarm: ```python title="Read Properties from Active Alarms" results = system.alarm.queryStatus(state=["ActiveUnacked", "ActiveAcked"]) for alarm in results: print str(alarm.getDisplayPath()), alarm.getState(), alarm.isAcked() ``` | Function | Description | Returned Object | |---|---|---| | getDisplayPath | Returns the Display Path of the alarm. | StringPath | | getDisplayPathOrSource | If the Display Path for the alarm is in an empty string, then returns the Source Path, otherwise, returns the Display Path | Python Unicode | | getId | Returns the UUID of the alarm event. | java.util.UUID | | getLastEventState | Returns the last state of the alarm. Possible return values are **Active**, **Acknowledged**, or **Cleared**. The last event is always returned, so if you're looking to see if an alarm is has been both Acknowledged and Cleared, use `getState()` instead. | AlarmStateTransition | | getName | Returns the name of the alarm. | Python Unicode | | getNotes | Returns the value of the Notes property. Returns a None-type object if a Note has not been configured on the Alarm. | Python Unicode or None | | getPriority | Returns an AlarmPriority object representing the Priority of the alarm. Can easily be converted to an Integer with .intValue. Default is String. | AlarmPriority | | getSource | Returns the Source path of the alarm. | QualifiedPath | | getState | Returns the current state of the alarm: i.e., Active, Unacknowledged | AlarmState | | isAcked | Returns a boolean flag indicating that the alarm has been Acknowledged. | Python Boolean | | isCleared | Returns a boolean flag indicating that the alarm has been Cleared. | Python Boolean | | isShelved | Returns a boolean flag indicating that the alarm has been Shelved. | Python Boolean | For the full list of methods, including the methods available to Script blocks in alarm pipelines, see the [PyAlarmEvent](appendix\reference-pages\scripting-object-reference\scripting-object-reference.md#pyalarmevent) section of the Scripting Object Reference page.
