Skip to main content
Version: 8.3
View as Markdown

IEC 61850 Driver

IEC 61850 is a protocol used for power systems that need to send control signals to different types of intelligent electronic devices (IEDs) defined in a substation. It is similar to the structure of the DNP3 protocol where a single station host can become a bridge to a web of other devices without taxing the network too much. For a more in-depth overview of IEC61850 standards and considerations, refer to the Understanding IEC61850 Knowledge Base article.

The Ignition driver acts as a 61850 Manufacturing Message Standard (MMS) Client. The IEC 61850 driver does NOT support Generic Object Oriented System Event (GOOSE) or Sampled Values (SV) protocols. Check your documentation to see whether your device supports IEC 61850.

note

The IEC 61850 driver only works on Windows and Linux (x64 distributions). ARM chips and macOS platforms are not currently supported.

In addition, the driver requires a modern version of the Visual C++ Redistributable. Read our technical advisory for more details: https://support.inductiveautomation.com/hc/en-us/articles/13897307938829

Connecting to a Device​

Inductive University

Connecting To IEC 61850 Devices

Watch the video

This module requires the OPC UA module to be installed and enabled. If the OPC UA module is not installed or is disabled, this module will fault with a warning in the logs and display the state as "Faulted Missing Dependency" on the Platform > System > Modules page.

Ignition's IEC 61850 driver can connect directly to any devices that support Ethernet communication through a substation host. It is important to make a new device connection for each of the substation device’s IEDs, since only one can be selected per connection.

  1. Go to the Connections section of the Gateway Webpage.

  2. Select Devices > Connections.

    Connecting to a Device Step 2

  3. Click on Create Device Connection.

  4. Scroll down to select the IEC 61850 MMS Client Driver and click Next.

    Connecting to a Device Step 4

  5. Enter a desired name into the Name field. In this example, we will be entering test.

  6. Enter the IP address or hostname of the device you are connecting to in the Hostname field. All other default settings can be left as is.

  7. Click Create Device Connection. The Device Connections page now lists the IEC 61850 MMS Client Driver. The Status column will show Connected or Idle, depending on the status of the device.

  8. On the connected driver, test in this example, and expand the three dots menu and select Manage SDL File.

    note

    Substation Configuration Description (SCD) files grant user control of transfer device descriptions and communication parameters. This file format is the only accepted System Configuration Language (SCL) file type. It is generally recommended to use an SCD file if you intend to limit the request size and visibility of access points during OPC browsing. This will effectively reduce the load against the substation device. Without an SCD file, any device connection restart will request all defined Logical Nodes from your defined IED for OPC browsing, which can become network-traffic heavy.

    However, because of how Ignition treats device attributes we recommend always using an SCD file, as it may not be possible to resolve associated quality or timestamp values without it.

    Connecting to a Device Step 8

  9. Locate your SCD file and drag it into the upload field or click the link to upload your file directly.

  10. Click Next.

    Connecting to a Device Step 11

  11. Select the IED you want to request for reports.

    Connecting to a Device Step 12

  12. Click Save Changes.

    info

    The Edit panel will now show the saved SCD file settings. Use SCD File will be checked, and IED Name and Access Point Name will match the selected upload config settings. You can use these settings to verify correct configuration or further tweak your SCD file.

Use the OPC Quick Client to Confirm Report Statuses​

Once you have established a device connection, you may want to verify report availability before opening the Designer. The OPC Quick Client provides a convenient way to inspect IEC 61850 report statuses and troubleshoot report configuration directly from the Gateway at Connections > OPC > Quick Client. From there, browse the Ignition OPC UA Server and locate your IED under the Devices folder, where configured IEC 61850 device data is organized into the following folders:

  • Model: Contains logical nodes that can be directly polled for information.
  • Reports: Contains a folder for each report control block, and exposes report-related attributes that can be subscribed to.
  • Diagnostics: Contains diagnostic information that can help identify the status of various aspects of the configured device.
note

Subscribing to any report control block attribute causes Ignition to attempt to enable the associated report using the RptEna attribute. If a report cannot be enabled, the subscription will return a quality of Bad_OutOfService: The source of the data is not operational.

If you are unsure if a report is enabled, you can use the [R] read action on the RptEna attribute within the appropriate report control block folder under Reports. A value of false indicates the report is not currently enabled, while a value of true indicates the report is already enabled elsewhere and cannot be enabled again.

Confirm Report Statuses

caution

The IEC 61850 standard permits very few write operations, and write actions should not be performed from the OPC Quick Client. See Device Operations for recommended practices when writing values back to an IED.

Device Properties​

General​

PropertyDescription
NameThe name of this IEC61850 device connection.
DescriptionDevice connection description (optional). Can be used to provide any useful information / comments about this connection.
EnabledIf True (checked), the connection is enabled; if False (unchecked), the connection is disabled.

Main​

PropertyDescription
HostnameThe IP Address of the device.
PortThe port to use when connecting to an IEC61850 device, default is 102.
Request TimeoutDetermines the maximum amount of time a request to the device will wait for a response, default is 2000.

SCD File Setting​

PropertyDescription
Use SCD FileDetermines if a SCD file upload will be used when requesting from the device. The default value is false.
Use Configured HostnameOverride any hostname that may have been set by the SCD file with the configured hostname, default is false.
Use Configured OSI ParamsOverride any OSI params that may have been set by the SCD file with the configured OSI params, default is false.
IED NameIf Use SCD File is enabled, this field will be populated automatically with the selected IED name during the SCD File Upload.
Access Point NameIf Use SCD File is enabled, this field will be populated automatically with the selected IED access point information during the SCD File Upload.

Advanced Client OSI Parameters​

PropertyDescription
Client AE QualifierSets the client Application Entity Qualifier, default is 12.
Client AP TitleSets the client Application Process Title, default is 1,1,1,999,1.
Client Presentation-SelectorSets the client Presentation-Selector (P-SEL), default is 00000001.
Client Session-SelectorSets the client Session-Selector (S-SEL), default is 0001.
Client Transport-SelectorSets the client Transport-Selector (T-SEL). It is optionally transmitted in the OSI Transport Layer connection request (CR), default is 0001.

Advanced Server OSI Parameters​

PropertyDescription
Server AE QualifierSets the server Application Entity Qualifier, default is 12.
Server AP TitleSets the server Application Process Title, default is 1,1,1,999,1.
Server Presentation-SelectorSets the server Presentation-Selector (P-SEL), default is 00000001.
Server Session-SelectorSets the server Session-Selector (S-SEL), default is 0001.
Server Transport-SelectorSets the server Transport-Selector (T-SEL). It is optionally transmitted in the OSI Transport Layer connection request (CR), default is 0001.

Misc. Advanced Settings​

PropertyDescription
Use Report TimestampDetermines if the timestamp from the report will be used instead of the timestamp associated with each reported value.
PasswordThe password selections available for the device connection. Options include None, Embedded, and Referenced. See the Secrets Management page for more information on using Referenced passwords.

Reports​

Reports can exchange monitoring information, power metering, power quality, and fault event analysis, among other data from IED servers to clients. Device data and reports are sent to the client based on user-defined device configuration through report control blocks (RCBs) and SCL files. The IEC 61850 driver supports Unbuffered/Buffered Report Control Blocks (URCB/BRCB). Remember, an RCB can only be enabled by a single device connection to the IED. This is because an RCB is blocked once a client has registered to receive a report by enabling it. Therefore, if the report is in use elsewhere, an attempted overlap could prevent connections from occurring. You will need to replicate the report on your IED if you want multiple Ignition Gateways to access the same report or leverage a Remote Tag Provider.

  • Buffered Reports: Reports are buffered by the IED in case a connection to the client is interrupted so that report data is still available to the client when the connection resumes.
  • Unbuffered Reports: Information is not stored during a connection loss, so any data that may have been sent during the lost connection time is not available. Reporting begins again after the connection has resumed.
note

If you are using a buffered report, be aware the config.idb file will be frequently updated with the last report_id received. The autobackup default time, set by the localdb.autobackup.delay property, is 60 minutes. A short delay, such as 2 minutes, could cause frequent backups and paused threads during the DB backup process. Changes to this property can be made in the data/gateway.xml file, and looks like the following:

<entry key="localdb.autobackup.delay">60</entry>

Changed in 8.3.8
Autobackups are now disabled by default. This means that changes to the localdb.autobackup.delay property will only apply when autobackups are enabled. Automatic backups are handled with localdb.autobackup.count.

Use the Tag Browser to Enable a Report​

Adding a report folder in your Designer immediately enables a report and allows you to see related attributes in the Tag Browser. This process is done in the same manner as creating a tag.

As you navigate to your desired Logical Node and Points folder, you'll notice a different format than what you might expect from a typical tag in the Tag Browser where all attributes are contained in a single tag. Attributes are listed as separate tags with their own qualified values (e.g. value, quality, and timestamps). This is because the Ignition needs to map the 61850 specification to the OPC UA model that requires an associated value, quality, and timestamp. Ignition will attempt to retrieve the q and t attributes that correspond with reported value attributes if they are available. Be sure to only add a single folder from the Points folder to your Tag Browser to avoid any issues that can occur from enabling multiple reports.

Use Tag Browser to Enable Report

Report Attributes​

Once a specific attribute tag has been added in the Connected Devices window, you'll see your enabled report data in the Tag Browser. You can further curate this data by deleting unwanted data from the browser display.

Report Attributes

IEC 61850 Hierarchical Data Model​

Additionally, the OPC item path that Ignition uses can be isolated to identify individual attribute data because paths are built with an hierarchical data model. The data included in the path identifies the IED, logical device, logical node, data object, and attribute information. The example attribute we've been using in this section is shown below.

[SSSA_52AFA_FPR]LD0/LLN0.rcbDigitals05$SSSA_52AFA_FPRCTRL/CBCILO1.EnaCls.stVal
  • IED: SSSA_52AFA_FPR
  • Logical Device: LD0/LLN0
  • Logical Node: rcbDigitals05$SSSA_52AFA_FPRCTRL/CBCILO1
  • Data Object: EnaCls
  • Attribute: stVal
Functional Constraints in OPC Addresses

Changed in 8.3.9
An attribute that is defined under more than one Functional Constraint (FC), such as a settable attribute exposed under SP, SE, and SG, is now browsed as a separate OPC node for each FC, rather than being collapsed into a single node. These colliding attributes are addressed with an [FC] suffix appended to the attribute, and reads and writes are directed to the FC named in the address:

[SSSA_52AFA_FPR]LD0/LLN0.rcbDigitals05$SSSA_52AFA_FPRCTRL/CBCILO1.EnaCls.stVal[ST]

On IEDs where these collisions exist, upgrading replaces the previous unsuffixed NodeIds with the [FC]-suffixed form. Existing tags addressed to the unsuffixed NodeId will report a quality of Bad_NodeIdUnknown after the upgrade, and must be re-addressed to the appropriate suffixed form. Attributes that are defined under only one FC are unaffected and keep their existing addresses.

Disable a Report​

Deleting all Points from the Tag Browser in your Designer and/or deleting all report point subscriptions from the OPC Quick Client page will disable a report. You can confirm a report is successfully disabled by using the read from link [r] for the corresponding RptEna tag on the OPC Quick Client page.

Additionally, if a device is disabled while a subscription is still active, the subscription status code will show Uncertain_LastUsableValue instead of the good value.

Device Operations​

Inductive University

Using IEC 61850 Scripting Functions

Watch the video

The IEC 61850 driver supports certain system functions to control operations and perform file services. These functions can be used to discover object data, test or maintain desired statuses, and modify device files. Check out the system.iec61850 page for complete function information.

Control Functions​

The supported IEC 61850 system control functions are getControlParams, Select, Operate, and Cancel. The getControlParams function returns a list of report control names and their attributes contained in the configured IEC 61850 device. Having a function to collect this data in the moment is useful for many instances, including to provide the required params keys for the Select, Operate, and Cancel functions if they are otherwise unknown.

The type of control model (ctlModel) defines how to use the Select (if applicable) and Operate control functions to write to the connected 61850 device when possible. A Status-only type means you cannot perform any operation actions. Direct types allow an immediate change to an access point using the Operate function only. Select before Operate (SBO) types require use of the Select function to confirm a chosen access point before the Operate function will run. Control model types are represented by the following values:

  • 0: Status-only
  • 1: Direct-with-normal -security
  • 2: SBO-with-normal-security
  • 3: Direct-with-enhanced-security
  • 4: SBO-with-enhanced-security

The Cancel function will clear a selection of an SBO type control if an operate command is not desired to be executed on the selected control.

Safety Considerations​

When working with the IEC 61850 system control functions, it's crucial to understand the potential safety implications. Misuse of these functions can lead to unintended operations and potentially catastrophic results for a high voltage substation.

Check Parameter, Control Interlock, and Synchrocheck

The Check parameter associated with system.iec61850.getControlParams is of critical importance for safety. Inside the Intelligent Electronic Device (IED) itself, there are logical nodes for interlocking and synchronizing, named Control Interlock (CILO) and Synchrocheck (RSYN). If the Check parameter is 00, the IED will ignore CILO and RSYN and execute the command even if there is an interlock activated or the grid is not synchronized with the generator speed. The results of not knowing this can be catastrophic for a high voltage substation. It is crucial for an integrator to be aware of this.

Select Function

The system.iec61850.select function is used to confirm a chosen access point before the Operate function will run. This is especially important for Select Before Operate (SBO) type controls. Misuse of this function can lead to unintended operations. Always ensure that the 'Check' parameter is properly set and understood before using this function, as it can influence the behavior of the Control Interlock (CILO) and Synchrocheck (RSYN) logical nodes in the Intelligent Electronic Device (IED).

Operate Function

The system.iec61850.operate function is used to write to the connected 61850 device when possible. However, it should be used with extreme caution. For Direct types, it allows an immediate change to an access point. For Select Before Operate (SBO) types, it should only be used after the Select function has confirmed the access point. Always ensure that the Check parameter is properly set and understood before using this function, as it can influence the behavior of the Control Interlock (CILO) and Synchrocheck (RSYN) logical nodes in the Intelligent Electronic Device (IED).

Cancel Function

The system.iec61850.cancel function will clear a selection of a Select Before Operate (SBO) type control if an operate command is not desired to be executed on the selected control. This function can be used as a safety measure to prevent unintended operations. Always ensure that the Check parameter is properly set and understood before using this function, as it can influence the behavior of the Control Interlock (CILO) and Synchrocheck (RSYN) logical nodes in the Intelligent Electronic Device (IED).

File Functions​

The supported IEC 61850 system file functions are listFiles, readFile, and writeFile. These functions allow users to obtain a list of files present on configured devices, and transfer IED files between remote IED servers and local paths. Note that local paths for file functions are local to the Gateway. For example, if these functions get used on a Perspective page, the file will be downloaded to the Gateway, not the client where the browser is running.