title: "Connecting to MicroLogix"
# Connecting to MicroLogix
## Connect to a MicroLogix Device
1. Go to the **Config** section of the Gateway Webpage.
2. Scroll down and select **OPC UA** > **Device Connections**.
3. On the **Devices** page, find the blue arrow and click on **Create new Device**.
4. Select **Allen-Bradley MicroLogix**, and click **Next**.
5. On the New Device page, leave all the default values and type in the following fields:
* **Name**: MLX
* **Hostname**: Enter **IP address** for the PLC, for example 10.20.7.77
6. Click **Create New Device**.
7. The **Devices** page is displayed showing the **MicroLogix** device is added to Ignition. The **Status** will show as Disconnected and then Connected.
8. To see all the tags, go to **OPC Client** > **Quick Client** in the **Config** section. On the **OPC Quick Client** page expand the **MicroLogix** folder which contains all the folders with the individual tags.
## Device Connection Settings
The **General** settings are common to all Allen-Bradley devices, and the **Connectivity** settings are device dependent.
### General Settings
| Name | Description |
| Name | The user-defined name for this Device. The name chosen will show up in **OPC Item Paths** and under **OPC-UA Server** > **Devices** of the **Configure** page of the Gateway. The Device Name must be alphanumeric. |
| Description | The user-defined description for the device. This is only used as a note to differentiate between devices. |
| Enable Device | Only devices that are enabled appear in **Connections > Devices** of the **Status** page of the Gateway and thus have their tags available for use. |
### Connectivity Settings
| Hostname | The Hostname value is the IP Address of the MicroLogix 1100 processor, MicroLogix 1400 processor or 1761-NET-ENI Ethernet interface. EthernetIP protocol on TCP port 44818 (0xAF12) is used to communicate to the listed devices. |
| Local Address | The local address to connect from when establishing a TCP connection. If left blank, then the driver will simply pick an available address. |
| Communication Timeout | After sending a request to the MicroLogix processor, the Communication Timeout setting is the amount of time in msec to wait for a response before treating it as a failure. |
| Browse Cache Timeout | When the data table layout is read from the MicroLogix processor, the Browse Cache Timeout value is the amount of time in msec to cache the results. |
### Advanced Settings
|Disable Processor Browse |Disables the processor browse setting. (Default is false.)|
|Zero TNS Connection| Disables the Zero TNS connection setting. (Default is false.)|
### Supported MicroLogix Connection Methods
* MicroLogix 1100 and 1400 direct
* MicroLogix 1100 and 1400 connected through 1761-NET-ENI
* MicroLogix 1100/1400 connected through Spectrum Controls WebPort 500
:::caution
MicroLogix 1200 and 1500 are not fully supported. Browsing is not available on these devices, so the 'Disable Processor Browse' advanced property will need to be set to True on the device connection.
Additionally, the MicroLogix driver can not access Input Parameters.
:::note
Some Micrologix devices may get stuck in a 'Browse Pending' status. In this case setting the connection path property to 1,0 should resolve the issue.