--- title: "Connecting to Logix" --- # Connecting to Logix > :::note > This driver is optimized for Logix family devices with firmware version 21+, but supports earlier firmware versions with significantly reduced performance. > ::: ## Connect to an Allen-Bradley Logix Device 1. Go to the **Config** section of the Gateway Webpage. 2. Scroll down and select **OPC UA** > **Device Connections**. ![Connect to Logix Step 2](connecting-to-logix-step-2.png) 3. On the **Devices** page, find the blue arrow and click on **Create new Device**. 4. Select **Allen-Bradley Logix Driver**, and click **Next**. ![Connect to Logix Step 4](connecting-to-logix-step-4.png) 5. Fill in the following fields: * **Name**: CLX * **Hostname**: type the **IP address** for the PLC, for example 10.20.1.54. Leave the default values in the remaining fields. ![Connect to Logix Step 5](connecting-to-logix-step-5.png) 6. Click **Create New Device**. 7. The **Devices** page is displayed showing the **ControlLogix** device is added to Ignition. The **Status** will show as Disconnected and then Connected. ![Connect to Logix Step 7](connecting-to-logix-step-7.png) 8. To see all the Tags, go to **OPC Client** > **Quick Client** in the **Config** section. On the **OPC Quick Client** page, expand the **CompactLogix** folder and in the **Global** folder you can see all the tags. ## Driver Implementation One noteworthy implementation of the Logix driver is how boolean arrays are handled. Boolean arrays items are browsed as members of a 32-bit DWORD. Thus, a BOOL[64] in the PLC is implemented as DWORD[2] in the driver. Below is a table representing how members of a boolean array items are mapped in the PLC, compared to the Logix driver's implementation. | PLC Mapping | Driver Implementation | |---|---| | boolTag[0] | boolTag[0].0 | | boolTag[31] | boolTag[0].31 | | boolTag[32] | boolTag[1].0 | | boolTag[63] | boolTag[1].31 | The Logix driver also supports the following datatypes: * DT (Date/Time) * LDT (Date/Time [ns]) * LTIME (LTime [ns]) * TIME (Decimal) * TIME32 (Time32 [us]) ## Device Connection Settings The General settings are common to all Allen Bradley devices, and the Connectivity settings are device dependent. ### General | Name | Description | |---|---| | Name | The user-defined name for this Device. The name chosen will show up in **OPC Item Paths** and under **OPC-UA Server** > **Devices** of the **Configure** page of the Gateway. The Device Name must be alphanumeric. | | Description | The user-defined description for the device. This is only used as a note to differentiate between devices. | | Enable Device | Only devices that are enabled appear in **Connections** > **Devices** of the **Status** page of the Gateway and thus have their tags available for use. | ### Connectivity | Name | Description | |---|---| | Hostname | This is the IP Address of the ControlLogix Ethernet module (1756-ENET) to route through to connect a ControlLogix processor. EthernetIP protocol on TCP port 44818 (0xAF12) is used to communicate to ControlLogix processors. | | Port | Port to connect to the remote device. | | Local Address | The local address to connect from when establishing a TCP connection. If left blank, then the driver will simply pick an available address. | | Timeout | After sending a request to the ControlLogix processor, the Communication Timeout setting is the amount of time in msec to wait for a response before treating it as a failure. | | Max Concurrent Requests | The number of requests that Ignition will try to send to the device at the same time. Increasing this number can sometimes help with your request throughput, however increasing this too much can overwhelm the device and hurt your communications with the device. | | Slot Number | The Slot Number value is the zero based ControlLogix chassis slot number of the ControlLogix processor to connect to. | |Connection Path| If specified, the slot number setting is ignored for this connection path to the processor. Be sure to terminate the path with backplane and slot number. | ### Advanced | Name | Description | |---|---| | Automatic Rebrowse | Monitor for tag additions and UDT changes and automatically initiate a re-browse when detected. If this is disabled tags will only be browsed when connecting and reconnecting. (Default is true.) | | Identity Request Frequency | Frequency, in milliseconds, that the request to read CIP Identity Object attributes occurs at. (Default is 5,000.) | | CIP Connection Size | The CIP connection size to use during Forward Open requests. (Default is 500.) | | CIP Connection Timeout | Target timeout, in milliseconds, for CIP connections and RPI. (Default is 16,000) |