--- title: "Connecting to ControlLogix" --- # Connecting to ControlLogix > >
:::caution This driver is intended for devices using ControlLogix firmware version 20 and older. ::: ## Connect to a Device 1. Go to the **Configure** section of the Gateway webpage. 1. Scroll down under **OPC-UA Server**, and click **Devices**. 1. On the **Devices** page, find the blue arrow and click on **Create new Device**. 1. On the **Add Device Step 1: Choose Type** page, select **Legacy Allen-Bradley ControlLogix**, and click **Next**. 1. On the New Device page, leave all the default values and type in the following fields: + Name: **CLX** + Hostname: type the **IP address** for the PLC 1. Click **Create New Device**. The Devices page is displayed showing the **ControlLogix** device is added to Ignition. The **Status** will show as Disconnected and then Connected. 1. To see all the tags, navigate to the **Configure** section of the gateway, and click on **Quick Client** under **OPC Connections**. On the **OPC Quick Client** page, expand the folder matching the name used in step 5, and expand the **Global** folder to see available tags. ![](CLXv20.png) ## Device Connection Settings The **General** settings are common to all Allen Bradley devices, and the **Connectivity** settings are device dependent. ### General Settings |Name|Description| |:---|:---| |Name|The user-defined name for this Device. The name chosen will show up in **OPC Item Paths** and under **OPC-UA Server > Devices** of the **Configure** page of the Gateway. The Device Name must be alphanumeric.| |Description|The user-defined description for the device. This is only used as a note to differentiate between devices.| |Enable Device|Only devices that are enabled appear in **Connections > Devices** of the **Status** page of the Gateway and thus have their tags available for use.| ### Connectivity Settings |Name|Description| |:---|:---| |Hostname|This is the IP Address of the ControlLogix Ethernet module (1756-ENET) to route through to connect a ControlLogix processor. EthernetIP protocol on TCP port 44818 (0xAF12) is used to communicate to ControlLogix processors.| |Timeout|After sending a request to the ControlLogix processor, the Communication Timeout setting is the amount of time in msec to wait for a response before treating it as a failure.| |Slot Number|The Slot Number value is the zero based ControlLogix chassis slot number of the ControlLogix processor to connect to.| |Connection Path|The Connection Path value is used to define the route to connect to the processor. The Connection Path format contains 4 numbers separated by commas. The first number is always 1 and tells the Ethernet module to route through the backplane. The rest of the numbers vary by device type, for a more in depth explanation of connection paths, see [Allen Bradley Connection Paths Explained section](opc-ua-and-device-connections\allen-bradley-ethernet\allen-bradley-ethernet.md#allen-bradley-connection-paths-explained).| |Concurrent Requests|The number of requests that Ignition will try to send to the device at the same time. Increasing this number can sometimes help with your request throughput, however increasing this too much can overwhelm the device and hurt your communications with the device.| ### Supported Connection Methods ControlLogix 5500 connected through 1756-ENET/A or 1756-ENET/B.
